 Post subject: Isolator Switches
PostPosted: Wed Nov 07, 2018 4:14 pm 
Offline
Homeless

Joined: Jan 8, 2016
Posts: 24
I've had conflicting advice on isolator switches in a new kitchen - we need six :(

Electrician is saying they need to go above the worktop in the kitchen. Architect says other electricians are more flexible putting them in utility rooms etc.

Looking at regs they seem to say that they must be "readily accessible", but there is no specific requirement that they are visible.

Hoping to put them in a small cupboard on the counter top, so they are readily accessible, but not visible.

Anyone seen the full regs?


Top
 Profile  
 
 Post subject: Re: Isolator Switches
PostPosted: Wed Nov 07, 2018 4:19 pm 
Offline
Too Big to Fail
User avatar

Joined: Aug 21, 2009
Posts: 4515
Location: Mesopotatia
notninety wrote:
I've had conflicting advice on isolator switches in a new kitchen - we need six :(

Electrician is saying they need to go above the worktop in the kitchen. Architect says other electricians are more flexible putting them in utility rooms etc.

Looking at regs they seem to say that they must be "readily accessible", but there is no specific requirement that they are visible.

Hoping to put them in a small cupboard on the counter top, so they are readily accessible, but not visible.

Anyone seen the full regs?



Not seen the full regs but readily accessible usually means identifiable and reachable. If someone who is not familiar with your kitchen needs to isolate the supply in an emergency then that's where you may have an issue. Theoretically you can do what you want in your own home and you my find a flexible electrician to put them in where you wish.

Most electrical products that are for fixed wiring are required to have an installation instruction that the disconnect device is easily accessible.

_________________
The real damage is done by those millions who want to 'get by'. The ordinary men who just want to be left in peace. Those who don’t want their lives disturbed by anything bigger than themselves. Those with no sides and no causes. Those who won’t take measure of their own strength, for fear of antagonizing their own weakness. Those people who roll up their spirits into tiny little balls so as to be safe. Safe?! From what?
Sophie Scholl


Top
 Profile  
 
 Post subject: Re: Isolator Switches
PostPosted: Wed Nov 07, 2018 6:08 pm 
Offline
Private Tenant

Joined: Jul 24, 2018
Posts: 41
notninety wrote:
I've had conflicting advice on isolator switches in a new kitchen - we need six :(

Electrician is saying they need to go above the worktop in the kitchen. Architect says other electricians are more flexible putting them in utility rooms etc.

Looking at regs they seem to say that they must be "readily accessible", but there is no specific requirement that they are visible.

Hoping to put them in a small cupboard on the counter top, so they are readily accessible, but not visible.

Anyone seen the full regs?


Can i ask is there a reason you need 6?


Top
 Profile  
 
 Post subject: Re: Isolator Switches
PostPosted: Wed Nov 07, 2018 6:29 pm 
Offline
Of Systemic Importance

Joined: Sep 13, 2012
Posts: 5311
Dubhgeannain wrote:
Theoretically you can do what you want in your own home

No you can't, or at least not legally, if they fall under the scope of Controlled Works (CER/15/249).

_________________
"It's easy to confuse what is with what ought to be, especially when what is has worked out in your favour"
Tyrion Lannister


Top
 Profile  
 
 Post subject: Re: Isolator Switches
PostPosted: Wed Nov 07, 2018 9:14 pm 
Offline
Too Big to Fail
User avatar

Joined: Aug 21, 2009
Posts: 4515
Location: Mesopotatia
Eschatologist wrote:
Dubhgeannain wrote:
Theoretically you can do what you want in your own home

No you can't, or at least not legally, if they fall under the scope of Controlled Works (CER/15/249).


Exactly :nin

_________________
The real damage is done by those millions who want to 'get by'. The ordinary men who just want to be left in peace. Those who don’t want their lives disturbed by anything bigger than themselves. Those with no sides and no causes. Those who won’t take measure of their own strength, for fear of antagonizing their own weakness. Those people who roll up their spirits into tiny little balls so as to be safe. Safe?! From what?
Sophie Scholl


Top
 Profile  
 
 Post subject: Re: Isolator Switches
PostPosted: Wed Nov 07, 2018 11:29 pm 
Offline
Homeless

Joined: Jan 8, 2016
Posts: 24
propertyspire wrote:
Can i ask is there a reason you need 6?


Oven, dishwasher, fridge, extractor, washing machine etc. Apparently they all need an isolator now.
Will ruin the backsplash, so not particularly happy cutting a hole for switches with red lights that are hardly ever used.


Wasn't sure on exact regs, and it seems to be some electricians will put them in a more discreet spot, but others won't. Mine won't, but was hoping to see the regs to see if it's just not recommended, or definitely not allowed.

Is it possible to have one isolator which isolates all the isolators, which could then be put in a less accessible spot?


Top
 Profile  
 
 Post subject: Re: Isolator Switches
PostPosted: Thu Nov 08, 2018 12:09 am 
Offline
Too Big to Fail

Joined: Aug 23, 2008
Posts: 3652
Location: Bogtrotterland!
notninety wrote:
propertyspire wrote:
Can i ask is there a reason you need 6?


Oven, dishwasher, fridge, extractor, washing machine etc. Apparently they all need an isolator now.
Will ruin the backsplash, so not particularly happy cutting a hole for switches with red lights that are hardly ever used.


Wasn't sure on exact regs, and it seems to be some electricians will put them in a more discreet spot, but others won't. Mine won't, but was hoping to see the regs to see if it's just not recommended, or definitely not allowed.

Is it possible to have one isolator which isolates all the isolators, which could then be put in a less accessible spot?

A kill switch for the kitchen, I suppose so. But you would still need separate switches for individual appliances.
The rules must have been tightened up in the past decade as in 2006, the electrician fitted the socket for the dishwasher in the next press.

_________________
"Democracy is like sausage, you want it, but you don't want to know how it is made". [John Godfrey Saxe]
Ronald Coase, Nobel Economic Sciences, said in 1991 “If we torture the data long enough, it will confess.”
"Give me control of a nation's money and I care not who makes it's laws" — Mayer Amschel Bauer Rothschild
"To be precise, my mistake. Humans are underrated": Elon Musk


Top
 Profile  
 
 Post subject: Re: Isolator Switches
PostPosted: Thu Nov 08, 2018 12:13 am 
Offline
Nationalised
User avatar

Joined: Jan 1, 1970
Posts: 23133
dolanbaker wrote:
notninety wrote:
propertyspire wrote:
Can i ask is there a reason you need 6?


Oven, dishwasher, fridge, extractor, washing machine etc. Apparently they all need an isolator now.
Will ruin the backsplash, so not particularly happy cutting a hole for switches with red lights that are hardly ever used.


Wasn't sure on exact regs, and it seems to be some electricians will put them in a more discreet spot, but others won't. Mine won't, but was hoping to see the regs to see if it's just not recommended, or definitely not allowed.

Is it possible to have one isolator which isolates all the isolators, which could then be put in a less accessible spot?

A kill switch for the kitchen, I suppose so. But you would still need separate switches for individual appliances.
The rules must have been tightened up in the past decade as in 2006, the electrician fitted the socket for the dishwasher in the next press.


I think things may have gone a bit too far if one anecdote from an electrician I heard recently is true. Turns out now if you get as much as a socket changed in the a kitchen the whole setup has to be re-certified again (RECI Cert).

A simple job ends up costing hundreds of euros.

BTW @OP, if you're not too happy, get a new electrician.

_________________
Follow The Pin - https://twitter.com/dailypinster

"Politicians are always realistically maneuvering for the next election. They are obsolete as fundamental problem-solvers." - Buckminster Fuller

"I was comfortable with a couple of banks being married today, instead i wake up and find I'm married to the banks." - Catbear

Image


Top
 Profile  
 
 Post subject: Re: Isolator Switches
PostPosted: Thu Nov 08, 2018 12:41 am 
Offline
Single Home Owner

Joined: Jan 27, 2014
Posts: 119
Easily accessible is what is required. Hob switch has to be very obvious, but an easily accessible cupboard at worktop height might be OK if you made it obvious that is where the switches are - eg a big sign...

More conventionally you could use an electrician who is familiar with mini-grid switches (don't put the hob isolator in it). You will probably need 2 in order to get all the cables in.


Top
 Profile  
 
 Post subject: Re: Isolator Switches
PostPosted: Thu Nov 08, 2018 1:31 am 
Offline
Nationalised
User avatar

Joined: Apr 1, 2010
Posts: 10774
This all sound completely nuts. A fridge draws barely more electricity than an incandescent light bulb. Many dishwashers draw no more current than a hair dryer. Separate isolator switches sounds like total overkill. I had no problem getting an electrician to mount the isolator for a hob and oven to the inside of an adjacent cupboard a few years back. Seems that things have changed.

Trying to actually look up the latest standards turns out to be a typical Irish joke. Google ET101 for more info. The "Electro-Technical Council of Ireland" website ( http://www.etci.ie) tells you that ETCI ceased trading. Not surprising seeing as Google cache tells you they were charging €106 for a copy of the ET101 standard. Lots of places (e.g. safeelectric.ie) still link to the defunct website. However, nsai.ie -- once you navigate past their page asking you to make an appointment to browse their standards database (!!! :shock: ) has a link to where you can supposedly buy it (in hardcopy only) for €5.70 ...

https://shop.standards.ie/en-ie/Standar ... I_2674776/

Klunkiest ordering system I ever saw, and the delivery options are DHL or Royal Mail :shock:

Are even our quangos being off-shored now?

_________________
"Prediction is very difficult, especially about the future" – Niels Bohr


Top
 Profile  
 
 Post subject: Re: Isolator Switches
PostPosted: Thu Nov 08, 2018 3:33 am 
Offline
Under CAB Investigation
User avatar

Joined: Sep 26, 2008
Posts: 1815
Location: Hey y'all
OP, ask the electrician who said you need isolator switches to show you the relevant regulation in the latest standards (as referenced above by ps200306 and which he should be carrying a copy of with him at all times) where it states you need an isolator on a 13(or 5)amp plug in appliance.

I will bet he can't, then you need to ask "do I need to get a qualified electrician in to check out what you have done as I am no longer confident in your understanding of the regulations" (if you want to act the bollix and get a serious discount that is :wink: ).

_________________
"Politics is the art of looking for trouble, finding it everywhere, diagnosing it incorrectly and applying the wrong remedies." —Groucho Marx


Top
 Profile  
 
 Post subject: Re: Isolator Switches
PostPosted: Thu Nov 08, 2018 3:11 pm 
Offline
Too Big to Fail
User avatar

Joined: Aug 21, 2009
Posts: 4515
Location: Mesopotatia
ps200306 wrote:
This all sound completely nuts. A fridge draws barely more electricity than an incandescent light bulb. Many dishwashers draw no more current than a hair dryer. Separate isolator switches sounds like total overkill. I had no problem getting an electrician to mount the isolator for a hob and oven to the inside of an adjacent cupboard a few years back. Seems that things have changed.

Trying to actually look up the latest standards turns out to be a typical Irish joke. Google ET101 for more info. The "Electro-Technical Council of Ireland" website ( http://www.etci.ie) tells you that ETCI ceased trading. Not surprising seeing as Google cache tells you they were charging €106 for a copy of the ET101 standard. Lots of places (e.g. safeelectric.ie) still link to the defunct website. However, nsai.ie -- once you navigate past their page asking you to make an appointment to browse their standards database (!!! :shock: ) has a link to where you can supposedly buy it (in hardcopy only) for €5.70 ...

https://shop.standards.ie/en-ie/Standar ... I_2674776/

Klunkiest ordering system I ever saw, and the delivery options are DHL or Royal Mail :shock:

Are even our quangos being off-shored now?


ETCI were subsumed by NSAI at the behest of the CER. It only ceased trading officially last year. There were was a lot of resistance from the old Technical Committee members and many didn't make the migration across to the new NSAI ETCs. I don't think the brain drain is the cause of the tightening of measures outlined above though.

Also just because a fridge doesn't consume as much electricity as an oven doesn't mean it's not as hazardous. See Grenfell Tower as an example.

I'd be interested to see the regs themselves but I'd be surprised if isolator switches are implicitly required as opposed to utilising the appliances plug. A plug acts as an equally suitable and even more secure disconnect device.

_________________
The real damage is done by those millions who want to 'get by'. The ordinary men who just want to be left in peace. Those who don’t want their lives disturbed by anything bigger than themselves. Those with no sides and no causes. Those who won’t take measure of their own strength, for fear of antagonizing their own weakness. Those people who roll up their spirits into tiny little balls so as to be safe. Safe?! From what?
Sophie Scholl


Top
 Profile  
 
 Post subject: Re: Isolator Switches
PostPosted: Thu Nov 08, 2018 3:41 pm 
Offline
Too Big to Fail
User avatar

Joined: Aug 21, 2009
Posts: 4515
Location: Mesopotatia
So I've managed to put my hands on the rules which came into effect September 2017. It's the 4th edition dated 2008

Quote:
554.3.5 A socket-outlet that is not readily accessible e.g. under or behind an appliance or a kitchen unit, shall be provided with a readily accessible means of isolation e.g. an isolating switch mounted nearby and suitably labelled


Not much room for interpretation there.

My kitchen would definitely have issues with this but then it was wired in 2000. Even labeling them now too. That's mentioned as a requirement elsewhere as well.

Specifically for ovens
Quote:
555.2.1 Where the oven and hob are separate appliances, a common supply and isolator may be used provided: Each appliance is within 2m of the switching device


2 m distance pops up all over the place with respect to isolation. Going back to what I know about product safety standards that is typically what is required by the manufactures of these devices too. So a kill all switch may not be feasible unless your kitchen is tiny.


What I don't see is an explicit requirement for a pilot light in the switches. Perhaps your electrician is more familiar with the regs but at least your kitchen won't be lit up like it's the festive season when you all the appliances on. So there's certain things that you assume are on all the time and don't need a light reminding you to the fact e.g. your fridge

_________________
The real damage is done by those millions who want to 'get by'. The ordinary men who just want to be left in peace. Those who don’t want their lives disturbed by anything bigger than themselves. Those with no sides and no causes. Those who won’t take measure of their own strength, for fear of antagonizing their own weakness. Those people who roll up their spirits into tiny little balls so as to be safe. Safe?! From what?
Sophie Scholl


Top
 Profile  
 
 Post subject: Re: Isolator Switches
PostPosted: Thu Nov 08, 2018 4:11 pm 
Offline
Private Tenant

Joined: Jul 24, 2018
Posts: 41
Can you get isolator switches that look like ordinary switches, im sure they dont all have to be ugly white swithces with red light?


Top
 Profile  
 
 Post subject: Re: Isolator Switches
PostPosted: Thu Nov 08, 2018 4:40 pm 
Offline
Too Big to Fail
User avatar

Joined: Aug 21, 2009
Posts: 4515
Location: Mesopotatia
propertyspire wrote:
Can you get isolator switches that look like ordinary switches, im sure they dont all have to be ugly white swithces with red light?


That's what I'm wondering too. I think you can. From amazon uk anyway

Image

That might be the best you can hope for OP. Of course you can get a nice chrome one either :D

This needs to be within 2 m of all your appliances though.

_________________
The real damage is done by those millions who want to 'get by'. The ordinary men who just want to be left in peace. Those who don’t want their lives disturbed by anything bigger than themselves. Those with no sides and no causes. Those who won’t take measure of their own strength, for fear of antagonizing their own weakness. Those people who roll up their spirits into tiny little balls so as to be safe. Safe?! From what?
Sophie Scholl


Top
 Profile  
 
Display posts from previous:  Sort by  
Post new topic Reply to topic  [ 16 posts ]  Go to page 1, 2  Next


Who is online

Users browsing this forum: Google Adsense [Bot] and 8 guests


You cannot post new topics in this forum
You cannot reply to topics in this forum
You cannot edit your posts in this forum
You cannot delete your posts in this forum

Jump to:  

Click for Latest Posts LATEST POSTS Click for Forum List FORUMS   

Follow, Retweet @dailypinster

  

Pyramid Built, Is Better Built!